Agreed. Posting from memory. I must have missed the 120/208 panel statement initially.So you are agreeing with my initial assessment in the previous post?
There is nothing in the original post that mentions neutrals at all. Could be 208V 3ph equipment. ofc (of course), all three conductors would be current-carrying then, and they'd also all be CCC with 208V 1ph with neutral. At least that is the assumption we both made as 45% applies to 21-30 CCC. In lieu of other pertinent information, like 'super sparky ran 10/3 to 208V lighting or water heaters' (that don't use a third CCC, hence we can ignore it for calculations), don't we have to assume that all 3 conductors are current carrying? The circuits come from a 208Y/120V 3ph panel.
eta: dunno about poorly worded, but I find it a terrible question nonetheless. Is there ANY real world application where the question would be applicable?
Real world application? Wouldn't put it past someone somewhere to try it.