The superintendent on the job is differing from my opinion on the "allowability" of MC cable in the walls I will paste the job specs below. I am not reading that MC cable is not allowed in the walls for receps etc. I believe he is reading into the Raceway section of the job specs about emt inside interior wall. I believe that since that it under the "Raceway" section of the specs it is only dealing with raceways themselves and not wiring methods, and it is my understanding that MC cable is not a raceway. Below are the pertinent specs. There is also the "shall be primarily used as whips", but all mc restricted jobs I have ran listed it as ONLY or under the "do not use". What is your professional opinions on this?
SECTION 260519 - LOW-VOLTAGE ELECTRICAL POWER CONDUCTORS AND CABLES
PART 2 - PRODUCTS
2.3 METAL-CLAD CABLE, TYPE MC
A. Description: A factory assembly of one or more current-carrying insulated conductors in an
overall metallic sheath. MC cable shall include grounding conductor.
B. Shall primarily be used as whips for connections to equipment and lighting not to exceed 6ft in
length.
2. Do Not Use MC Cable for the Following:
a. Homeruns to panelboards.
b. Where exposed to view.
c. Where exposed to damage.
d. Hazardous locations.
e. Wet locations.
f. When restricted otherwise above, and when specifically disallowed by the local
AHJ or Owner.
g. Circuits supplied by an emergency or standby power source.
3. Aluminum sheathing for MC Cable is not allowed.
SECTION 260533 - RACEWAYS AND BOXES FOR ELECTRICAL SYSTEMS
PART 3 - EXECUTION
3.1 RACEWAY APPLICATION
B. Indoors: Apply raceway products as specified below unless otherwise indicated:
1. Exposed, Not Subject to Physical Damage: EMT.
2. Exposed, Not Subject to Severe Physical Damage: EMT unless noted otherwise.
3. Exposed and Subject to Severe Physical Damage: GRC. Raceway locations include th
following:
a. Loading dock.
b. Corridors used for traffic of mechanized carts, forklifts, and pallet-handling units.
c. Mechanical rooms.
d. Gymnasiums.
4. Concealed in Ceilings and Interior Walls and Partitions: EMT.
SECTION 260519 - LOW-VOLTAGE ELECTRICAL POWER CONDUCTORS AND CABLES
PART 2 - PRODUCTS
2.3 METAL-CLAD CABLE, TYPE MC
A. Description: A factory assembly of one or more current-carrying insulated conductors in an
overall metallic sheath. MC cable shall include grounding conductor.
B. Shall primarily be used as whips for connections to equipment and lighting not to exceed 6ft in
length.
2. Do Not Use MC Cable for the Following:
a. Homeruns to panelboards.
b. Where exposed to view.
c. Where exposed to damage.
d. Hazardous locations.
e. Wet locations.
f. When restricted otherwise above, and when specifically disallowed by the local
AHJ or Owner.
g. Circuits supplied by an emergency or standby power source.
3. Aluminum sheathing for MC Cable is not allowed.
SECTION 260533 - RACEWAYS AND BOXES FOR ELECTRICAL SYSTEMS
PART 3 - EXECUTION
3.1 RACEWAY APPLICATION
B. Indoors: Apply raceway products as specified below unless otherwise indicated:
1. Exposed, Not Subject to Physical Damage: EMT.
2. Exposed, Not Subject to Severe Physical Damage: EMT unless noted otherwise.
3. Exposed and Subject to Severe Physical Damage: GRC. Raceway locations include th
following:
a. Loading dock.
b. Corridors used for traffic of mechanized carts, forklifts, and pallet-handling units.
c. Mechanical rooms.
d. Gymnasiums.
4. Concealed in Ceilings and Interior Walls and Partitions: EMT.