jcook980
Member
- Location
- Gresham, Oregon
- Occupation
- Electrical Engineer
iwire said:The 2002 also had a listed for the purpose requirement.
Nope, it simply required it to be listed. Check the wording in the 2002 Code carefully. The way it was worded then, any listed ground fault device was acceptable. The committee re-wrote that section to require the ground fault device to be specifically listed to protect the EGC. Since that is never going to happen, the edit effectively eliminates this means of protecting the EGC.
Here's the 2005 ROP:
5-231a Log #CP504 NEC-P05
(250-122(F)(2)3)
Final Action: Accept
Submitter: Code-Making Panel 5
Recommendation:
In 250.122(F)(2)(3) Change the words "listed for the purpose" to "... listed for the purpose of protecting the equipment grounding
conductor."
Substantiation:
The panel revised the text to remove vague unenforceable term " ? for the purpose ?", improve clarity, and comply with the NEC Style
Manual 3.2.1.
Panel Meeting Action: Accept
Number Eligible to Vote: 16
Ballot Results: Affirmative: 16
Comment on Affirmative:
SKUGGEVIG: Correlation with Proposal 5-1 regarding changing the term "equipment grounding conductor" to "equipment bonding
conductor" will be needed.