MC cable hospital grade ground wire

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
If you can use hospital grade MC cable sheathing as a equipment grounding conductor, do I even need to attach/use the green wire? Thank you for your help.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
If you mean using health care grade MC in a non health care situation where redundant grounding is not required?

I believe that if an EGC is present it needs to be used.

Jon
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
If you can use hospital grade MC cable sheathing as a equipment grounding conductor, do I even need to attach/use the green wire? Thank you for your help.
You either need to ground it or cap it in case it becomes energized.

Sent from my BE2028 using Tapatalk
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
If you can use hospital grade MC cable sheathing as a equipment grounding conductor, do I even need to attach/use the green wire? Thank you for your help.

Why would you not?
 