Is it permissible to install MC cable in the hallway of a hospital to feed a new 240-volt coffee machine in the employee lounge. It will not pass thru ANY patient areas. If it is allowed, does it have to be medical grade MC.? I am not sure on this.
 
517.13 wiring methods apply to circuits supplying patient care areas. If your circuit does not supply patient care standard MC would be acceptable
 