Already answered in post #9.
250.118(11)
392.7(B)
Table 392.7(B)
I thought single conductors vs. MC cable might make a difference. But looking at your references, it does look like the tray could be used as the sole ground, in either case. (We still won't do this, just like we wouldn't normally use EMT as the only ground).
Steve,
I have been told that sometimes it is cheaper to order a 4 conductor cable in place of the 3 conductor cable with the larger EGC. You would just not use the EGC in the 4 conductor cable.
I had actually wondered about that. It probably depends a lot on the size of the wire. It's hard to believe an extra 350KCM wire is going to be cheaper than a #1. But I might list that as an option.
I guess with the wire being 350KCM, there wouldn't be any problem with the color of the wire? The electricians would just tape the end with green tape?
Steve