- Illinois
- retired electrician
Try 300.3(B).So where in the code does it say be it more than one or a combination of 250.118 EGC's, that such must be contained within the sheath of an MC cable?
OK... [I have a sneaking suspicion I've been down this path before :grin: ]don_resqcapt19 said:Try 300.3(B).
Smart $ said:OK... [I have a sneaking suspicion I've been down this path before :grin: ]
... but 300.3(B) states the EGC "shall be contained within the same raceway, ...cable tray, ...cable, or cord, unless..."
1.) What would be your interpretation if it were a parallel run of plain ol' 3-conductor without ground tray cable?iwire said:I will agree that is a poorly written section.
1.) If I was the inspector AHJ my interpretation would be that the conductors including the EGC be contained within the same metallic sheath.
2.) But that is irrelevant to a technical guy like you.![]()
3.) Steve was not talking about the EGC being contained in the cable tray he was talking about using the cable tray as the EGC.