MC cable in wood studs

Status
Not open for further replies.

jonny1982

Member
Location
CA
How many 12-2 MC cables can be ran through a single hole in a 2 x 4 wood stud? I know with romex it is 3. Is it different for MC cable?

Thanks!
 
How many 12-2 MC cables can be ran through a single hole in a 2 x 4 wood stud? I know with romex it is 3. Is it different for MC cable?

Thanks!

How big is the hole ? Seriously when using a 3/4" or 7/8" hole drilled in a wood stud One per hole would be what I would do.
Fifteen Years Ago
A green helper (he knew enough to be dangerous) drilled all of the basement joist with a 2 1/4" self feed bit. Still 3 cables max is all that were allowed through these holes. Needless to say some of his holes were too close to the edge & sister joist had to be installed.
 
How many 12-2 MC cables can be ran through a single hole in a 2 x 4 wood stud? I know with romex it is 3. Is it different for MC cable?

Thanks!

Running cables through a hole is not automatically considered bundling if there is air space between the cables in the areas between the studs. Also there is no 3 cable limit for NM cable.
 
Do stud holes have to be 2" apart like joist holes? and johny1982, you could get a few sections of your 12-2/3 MC and drill holes in a scrap of 2x4 to see how easy they are to pull thru. A drill bit that leaves clean holes (no splinters on the backside) will make cable pulling a lot easier regardless the cable type.
 
Running cables through a hole is not automatically considered bundling if there is air space between the cables in the areas between the studs. Also there is no 3 cable limit for NM cable.
Agree, also don't know where people keep coming up with 3 cable limit. If you do require ampacity adjustment most of the time you can still have 4 cables before you need to upsize anything, unless there is more then two current carrying conductors in any of the cables. The key here is number of current carrying conductors not number of cables.
 
Running cables through a hole is not automatically considered bundling if there is air space between the cables in the areas between the studs.

I am not sure the NEC agrees with you.


Consider that the NEC considers MC run through bridal rings as bundling as evidenced by this.

d. Not more than 20 current-carrying conductors are installed
without maintaining spacing, are stacked, or are
supported on“bridle rings.”

Notice it says without maintaining spacing OR supported on bridal rings.

In my mind running through a stud every 16" is much more bundled than running through a bridal ring perhaps every 6'
 
I am not sure the NEC agrees with you.


Consider that the NEC considers MC run through bridal rings as bundling as evidenced by this.



Notice it says without maintaining spacing OR supported on bridal rings.

In my mind running through a stud every 16" is much more bundled than running through a bridal ring perhaps every 6'

I would disagree, just because that section mentions bridle rings does not mean it applies to all similar installations like running through stud holes. Although I do agree with your logic it simply says that if you use bridle rings then you consider them bundled.
 
I would disagree, just because that section mentions bridle rings does not mean it applies to all similar installations like running through stud holes. Although I do agree with your logic it simply says that if you use bridle rings then you consider them bundled.

How can something held loosely together every 6' be bundling while something tightly bundled every 16" is not?

I can't follow that logic.
 
How can something held loosely together every 6' be bundling while something tightly bundled every 16" is not?

I can't follow that logic.

Same here, I also think the could use a little work to clarify better. Use of bridal ring in the wording is too specific for something likely intended to be more general in nature. If it said "including but not limited to ... or similar" it would be some improvement.
 
How can something held loosely together every 6' be bundling while something tightly bundled every 16" is not?

I can't follow that logic.

I agree with your logic but what you're saying (that the cables between the studs are bundled) is not supported by any wording in 310.15(B)(3)(a). In fact the section that you've mentioned is a specific allowance to the modify the derating required by the first paragraph in 310.15(B)(3).

Bridle ring installations only fall within that allowance {310.15(B)(3)(a)(4)} for #12 MC or AC cables and is not applied universally to all installations under 310.15(B)(3)(a).

If that section had some wording similar to what Kwired mentioned then I would agree but currently it does not and is therefore not enforceable.
 