herding_cats
Senior Member
- Location
- Kansas
- Occupation
- Mechanical Engineer
I did. I told them to stop doing this and either land a box, or transition fitting.
That's the other issue: no strain relief. It's not bonded.For normal MC cable, the armor does not serve as the equipment grounding conductor.
The problems that I have either the installation as described by the OP are:
How are the conductors protected from the armor without an MC connector at the end point?
If this is MC-AP, how is the EGC bonded?
Is there anything providing strain relief on the terminations in the box if the MC gets tugged.
That's the other issue: no strain relief. It's not bonded.
Uh, see post #2.I'd argue that ordinary MC doesn't need the sheath bonded, because the sheath isn't an EGC.
2017 NEC 250.96(A) says "Metal raceways, cable trays, cable armor, cable sheath, enclosures, frames, fittings, and other metal non–
current-carrying parts that are to serve as equipment grounding conductors, with or without the use of supplementary equipment grounding conductors, shall be bonded where necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them."
Cheers, Wayne
The former.Does the clause 'that are to serve as equipment grounding conductors' apply only to 'other metal non-current-carrying parts', or does that clause apply to the complete list of metal parts?
Neither the MC armor, nor the EMC, is intended (in this case) to serve as an EGC, so I don't think it would need bonding.The former.
The latter you'd write as "Metal non–current-carrying parts that are to serve as equipment grounding conductors, including metal raceways, cable trays, cable armor, cable sheath, enclosures, frames, and fittings . . ."
Cheers, Wayne
It's actually prohibited for use as an EGC. That's the purpose of the green conductor. The reason that the armor needs to be bonded is because it is conductive and could become energized much like metallic plumbing etc. Normally this bonding occurs automatically through the use of listed MC connectors and metallic boxes, the boxes being bonded to the green EGC with a ground screw.I'd argue that ordinary MC doesn't need the sheath bonded, because the sheath isn't an EGC.
That is done all the time with NM cable when dropping down say a masonry wall on the surface. You still would be required to attach the EGC to the box at the other end.Here’s what they were doing:
Yeah it just sounds super hack, if one of our guys pulled MC into a raceway it would immediately get pulled out and redone.hack work.
-Hal
You stop just short of the box with the EMT and put an NM connector on the top of box for the cable. The EMT in this case does not get bonded. You have sleeved the cable.That is done all the time with NM cable when dropping down say a masonry wall on the surface. You still would be required to attach the EGC to the box at the other end.
I get that and agree that it would be code compliant to not bond the EMT.You stop just short of the box with the EMT and put an NM connector on the top of box for the cable. The EMT in this case does not get bonded. You have sleeved the cable.
-Hal
That is done all the time with NM cable when dropping down say a masonry wall on the surface. You still would be required to attach the EGC to the box at the other end.
There are two ways to do this:That is done all the time with NM cable when dropping down say a masonry wall on the surface.
That qualifier only applies to "other non-metal current carrying parts." MC cable armor always needs bonding. Of course, the picture doesn't show what is happening at the other end of MC cable, so it may be bonded there.Neither the MC armor, nor the EMC, is intended (in this case) to serve as an EGC, so I don't think it would need bonding.
I said the MC wasn't terminated properly. My statement was the armor, and EMT, was not intended to serve as the EGC.That qualifier only applies to "other non-metal current carrying parts." MC cable armor always needs bonding. Of course, the picture doesn't show what is happening at the other end of MC cable, so it may be bonded there.
Cheers, Wayne
Agreed, but it still needs bonding, which is what I believe 250.96(A) is saying, and what my post you quoted was saying.I said the MC wasn't terminated properly. My statement was the armor, and EMT, was not intended to serve as the EGC.
334.15 also allows running a raceway down the wall, with just a bushing at the open end and directly entering a box on the other end with appropriate termination method for the type of raceway being used. I don't believe there is such an allowance for MC or AC cable though. This does say in unfinished basements and crawl spaces in 2023 NEC. Not sure it it was always basements and crawl spaces, I've done it in other locations as well when you have some sort of wall you can not easily conceal wiring in yet you primarily are running NM cable at the premises.There are two ways to do this:
1) Put an NM (MC) to EMT transition connector at the top of the EMT and an EMT connector where it connects to the box.
2) Sleeve the NM (MC). Run the cable through a piece of EMT and stop short of the box where you use an NM or MC connector.
Each is acceptable and which one you use depends on the installation. Generally, the transition connector is used in commercial, sleeving is seen more in residential where damage is less likely.
-Hal