MC Cable rated for underground non-PVC coated

Merry Christmas

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
NYC electrical code says that I cannot use PVC coated underground MC cable in residential buildings with 3+ units.

Is there any MC cable out there that is rated for underground that is not PVC coated?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
NYC electrical code says that I cannot use PVC coated underground MC cable in residential
Good information. Probably doesn’t last long, and listed fittings are cost prohibitive.
Is there any MC cable out there that is rated for underground that is not PVC coated?
Wrap with stretch and seal silicon tape
 

Attachments

  • IMG_1555.jpeg
    IMG_1555.jpeg
    30.2 KB · Views: 5

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
To clarify, the cable is a power cable
McDonald’s Douglas technical orders specified the Milspec version of this tape for F-15c wiring harnesses in pylons, subject to corrosive atmospheres at Mach 2.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
FWIW, UL Standard 1569 on MC Cable lists in Table 10 a variety of outer jacket materials that may be used, including CP, CPE, ETFE, ECTFE, NBR/PVC, Neoprene, PVC, LDFRPE, HDFRPE, TPE, and XL. No idea which if any of those are commercially available.

Cheers, Wayne
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Some products are marketed as having a LSZH jacket (low smoke zero halogen), so that's a possible search to try.

Cheers, Wayne
 
NYC electrical code says that I cannot use PVC coated underground MC cable in residential buildings with 3+ units.

Is there any MC cable out there that is rated for underground that is not PVC coated?
So I assume this is under a slab? IF so then isnt it "outside" per 230.6? Does the NYC code make a distinction between "outside' and "under" a building?
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
So I assume this is under a slab? IF so then isnt it "outside" per 230.6? Does the NYC code make a distinction between "outside' and "under" a building?
The cable is a feeder. Article 230 are not for feeders though.
So, why would you use underground cable in the building? Simply transition to regular MC where it enters.

-Hal
Because there is no headroom inside the building cellar where the wires need to go. And I want to avoid transitioning because it will require splice boxes and I am trying to avoid splice boxes at all cost.

I have an idea. I will just chop existing concrete on the floor and make the floor hollow 2 hour rated with steel landing on top of the 2 hour fire rated floor. That way the cables are not underground in concrete, they are just in a hollow area below the floor. The run is going to be really short maybe like 4-6 feet
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have an idea. I will just chop existing concrete on the floor and make the floor hollow 2 hour rated with steel landing on top of the 2 hour fire rated floor. That way the cables are not underground in concrete, they are just in a hollow area below the floor.
You can just put them in a shallow groove in the concrete and patch over them. In the slab is not underground.
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
You can just put them in a shallow groove in the concrete and patch over them. In the slab is not underground.
As long as it's not in concrete that works too. Honestly I think it's better to chop the floor larger than a groove so that the wires can breath better. I can put steel floor on top so no one can walk over the cables
 