That's not a cable...Yes there is. It's called Galvanized Rigid Conduit.
Good information. Probably doesn’t last long, and listed fittings are cost prohibitive.NYC electrical code says that I cannot use PVC coated underground MC cable in residential
Wrap with stretch and seal silicon tapeIs there any MC cable out there that is rated for underground that is not PVC coated?
I don't know if you're serious or joking... lolWrap with stretch and seal silicon tape
McDonald’s Douglas technical orders specified the Milspec version of this tape for F-15c wiring harnesses in pylons, subject to corrosive atmospheres at Mach 2.To clarify, the cable is a power cable
No. It's all PVC coated if it can go underground.NYC electrical code says that I cannot use PVC coated underground MC cable in residential buildings with 3+ units.
Is there any MC cable out there that is rated for underground that is not PVC coated?
So I assume this is under a slab? IF so then isnt it "outside" per 230.6? Does the NYC code make a distinction between "outside' and "under" a building?NYC electrical code says that I cannot use PVC coated underground MC cable in residential buildings with 3+ units.
Is there any MC cable out there that is rated for underground that is not PVC coated?
So, why would you use underground cable in the building? Simply transition to regular MC where it enters.NYC electrical code says that I cannot use PVC coated underground MC cable in residential buildings with 3+ units.
The cable is a feeder. Article 230 are not for feeders though.So I assume this is under a slab? IF so then isnt it "outside" per 230.6? Does the NYC code make a distinction between "outside' and "under" a building?
Because there is no headroom inside the building cellar where the wires need to go. And I want to avoid transitioning because it will require splice boxes and I am trying to avoid splice boxes at all cost.So, why would you use underground cable in the building? Simply transition to regular MC where it enters.
-Hal
You can just put them in a shallow groove in the concrete and patch over them. In the slab is not underground.I have an idea. I will just chop existing concrete on the floor and make the floor hollow 2 hour rated with steel landing on top of the 2 hour fire rated floor. That way the cables are not underground in concrete, they are just in a hollow area below the floor.
As long as it's not in concrete that works too. Honestly I think it's better to chop the floor larger than a groove so that the wires can breath better. I can put steel floor on top so no one can walk over the cablesYou can just put them in a shallow groove in the concrete and patch over them. In the slab is not underground.
True however that criteria is used for other than service conductors as wellThe cable is a feeder. Article 230 are not for feeders though.
Hmmm What makes you say that? Need proofTrue however that criteria is used for other than service conductors as well
I know, trust but verify. 225.32, 240.21(B)(5), 240.21(C)(4), 240.92(D)Hmmm What makes you say that? Need proof