MC Cable rated for underground non-PVC coated
Tainted
New York
Engineer (PE)
NYC electrical code says that I cannot use PVC coated underground MC cable in residential buildings with 3+ units.
Is there any MC cable out there that is rated for underground that is not PVC coated?
Good information. Probably doesn’t last long, and listed fittings are cost prohibitive.
Wrap with stretch and seal silicon tape
FWIW, UL Standard 1569 on MC Cable lists in Table 10 a variety of outer jacket materials that may be used, including CP, CPE, ETFE, ECTFE, NBR/PVC, Neoprene, PVC, LDFRPE, HDFRPE, TPE, and XL. No idea which if any of those are commercially available.
Cheers, Wayne
Some products are marketed as having a LSZH jacket (low smoke zero halogen), so that's a possible search to try.
Cheers, Wayne
So I assume this is under a slab? IF so then isnt it "outside" per 230.6? Does the NYC code make a distinction between "outside' and "under" a building?
The cable is a feeder. Article 230 are not for feeders though.
So, why would you use underground cable in the building? Simply transition to regular MC where it enters.
-Hal
Because there is no headroom inside the building cellar where the wires need to go. And I want to avoid transitioning because it will require splice boxes and I am trying to avoid splice boxes at all cost.
I have an idea. I will just chop existing concrete on the floor and make the floor hollow 2 hour rated with steel landing on top of the 2 hour fire rated floor. That way the cables are not underground in concrete, they are just in a hollow area below the floor. The run is going to be really short maybe like 4-6 feet
You can just put them in a shallow groove in the concrete and patch over them. In the slab is not underground.
As long as it's not in concrete that works too. Honestly I think it's better to chop the floor larger than a groove so that the wires can breath better. I can put steel floor on top so no one can walk over the cables