We are doing a lot of tenant improvements recently where they like to have offices with t-bar grid and hallways with no ceiling. I like to run a 10' stick of 2" EMT across the hallway and use it to run MC between offices. Here is the question:
If I run say eight 12-3 cables (24 current carrying conductors) through this EMT, then per Exception to (4) of 310.15(B)(3)(a)(4) I would have to derate the circuits to 18 amps (60% of 30 amps). Then, per 240.4(B) I can put these circuits on a 20 amp breaker (next higher standard breaker). The circuits will have been designed to maximum of 16 amps (per 210.19(A)(1).
Does this sound code compliant?
Thanks
If I run say eight 12-3 cables (24 current carrying conductors) through this EMT, then per Exception to (4) of 310.15(B)(3)(a)(4) I would have to derate the circuits to 18 amps (60% of 30 amps). Then, per 240.4(B) I can put these circuits on a 20 amp breaker (next higher standard breaker). The circuits will have been designed to maximum of 16 amps (per 210.19(A)(1).