MC cable run though an emt raceway

Status
Not open for further replies.
Are all 24 conductors "current carrying"? If these are 120/240 MWBC's the neutrals don't count as current carrying for ampacity adjustments. If it is 120/208 MWBC's neutral does count as a current carrying conductor.

Just something to consider.

If the neutrals are not CCC's then no derating is required. :)
 
Status