Why did you think that? If it's run vertically in the stud wall you would strap it at intervals not exceeding 6'. If it's run horizontally through the holes it's considered supported.I thought MC cable did not need to be supported every 6' within stud
Then nothing is required.Yes I meant horizontally through the stud ko's
Except within 12" of box?Then nothing is required.