Can type MC cable be installed into a PVC junction box?
I would say that is in violation of the 2005 NEC but cannot find where it would be. I've looked in 250 and 330.
I have had it suggested to me that this is not a violation and have been asked to install the MC this way.
Is it a violation and where can I find the article.
Thanks
Tim
Re: MC cable terminated in PVC box
Perfect.
Exactly what I was looking for.
Thanks
Tim
The way I read it it is a violation to use MC with a PVC box unless you use bonding bushings per exception 1.