We are supposed to upsize the equipment grounding conductor if there is voltage drop.
MC cables have preinstalled equipment grounding conductors in them so the only way to get the correct equipment grounding conductor size is to get a significantly larger MC cable with larger phase conductors for the correct equipment grounding conductor size...
Is there a way to get custom MC cable with any equipment grounding conductor size?
for example cable with #2 phase conductors and with #2 equipment grounding conductor?
A typical #2 cable only comes with #6 equipment grounding conductor size but I need it to be #2
MC cables have preinstalled equipment grounding conductors in them so the only way to get the correct equipment grounding conductor size is to get a significantly larger MC cable with larger phase conductors for the correct equipment grounding conductor size...
Is there a way to get custom MC cable with any equipment grounding conductor size?
for example cable with #2 phase conductors and with #2 equipment grounding conductor?
A typical #2 cable only comes with #6 equipment grounding conductor size but I need it to be #2