An installation consists of PVC Enclosures with standard corrugated sheath MC run between the enclosures. I am of the opinion that steps must be taken to bond the MC based on 250.86. Any input ?
I agree with Don and Bob. Not sure what the solution is unless the box meets Don's code section.
How would you bond it?
Small bonding nut on an appropriate MC connector?
How would you bond it?
Small bonding nut on an appropriate MC connector?
Yes the sheath still needs a connection to ground even if it is not being used as an EGC.
Don pointed out a good code reference.
I agree with Don and Bob. Not sure what the solution is unless the box meets Don's code section.
Wonder why they used PVC boxes with MC anyway?
If you run MC into the box chances are there will be splices to connect to the MC cable.a bonding lock nut or washer inside the pvc box, tied to gnd? assumed the box is a jb and not just a pull box. if a pull box then you'll need to splice the gnd, or, move to metal.
very true, very true. my mind was not in "MC" modeIf you run MC into the box chances are there will be splices to connect to the MC cable.
What is the difference? Are those terms defined in the NEC?Augie mentioned PVC enclosures, Don's reference is for boxes. Are the requirements the same for boxes and enclosures?