No it does not have to do with MC wires bundled together in a panelOriginally posted by sbe:
310.15(B)(2) Exception No.5 refers to the use of MC wires bundled together in a panel
sbe follow Dons link, he has the correct answer to this question.Originally posted by sbe:
In other words, no derating is required for these wires located & bundled within the panel board.![]()
Take a look at part (a) it says "cable" once stripped it is no longer a cable it is conductors and part (c) I have not seen bridle rings used in a panel.Exception No. 5: Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket under the following conditions:
(a)Each cable has not more than three current-carrying conductors.
(b)The conductors are 12 AWG copper.
(c)Not more than 20 current-carrying conductors are bundled, stacked, or supported on ?bridle rings.?
A 60 percent adjustment factor shall be applied where the current-carrying conductors in these cables that are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing exceeds 20.
Bob310.15(B)(2)Adjustment Factors.
(a)More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(2)(a).