J j rae Senior Member Oct 3, 2007 #1 If you can get MC cable with an insilated ground whats the difference between regular MC vs. Hospital grade??
If you can get MC cable with an insilated ground whats the difference between regular MC vs. Hospital grade??
rcarroll Senior Member Location Fort Collins, Colorado Oct 3, 2007 #2 Whether or not the outer sheathing of mc cable is listed & identified as an equipment grounding conductor. 250.118
Whether or not the outer sheathing of mc cable is listed & identified as an equipment grounding conductor. 250.118
kid_stevens Senior Member Location Albuquerque, NM Oct 3, 2007 #3 Hospital circuits require a ground path and a shell bonded path that are isolated from one another. MC by default does not provide a ground path in the shell by default.
Hospital circuits require a ground path and a shell bonded path that are isolated from one another. MC by default does not provide a ground path in the shell by default.
Energize Senior Member Location Milky Way Galaxy Oct 3, 2007 #4 Is a MCcable anything like a MCmuffin?:grin:
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Oct 3, 2007 #5 There is a newer type of MC cable called MC AP that is a cross between AC and MC. It saves 30% on installation as there is no EGC to make up.
There is a newer type of MC cable called MC AP that is a cross between AC and MC. It saves 30% on installation as there is no EGC to make up.
kid_stevens Senior Member Location Albuquerque, NM Oct 3, 2007 #6 Energize said: Is a MCcable anything like a MCmuffin?:grin: Click to expand... Does that muffin have nuts in it?
Energize said: Is a MCcable anything like a MCmuffin?:grin: Click to expand... Does that muffin have nuts in it?
Jim W in Tampa Senior Member Location Tampa Florida Oct 3, 2007 #7 Regular mc lacks a redundant ground
peter d Senior Member Location New England Oct 3, 2007 #8 Hospital Grade "MC" is actually Type AC cable, since as the others have mentioned, the armor of MC cable is not listed for grounding.
Hospital Grade "MC" is actually Type AC cable, since as the others have mentioned, the armor of MC cable is not listed for grounding.