MC Exposed

Merry Christmas
Status
Not open for further replies.

blue spark

Senior Member
Location
MN
I was always under the assumption MC could not be run exposed to physical damage. In utility rooms I use it for whips to the mechanicals but thats a little different. Yesterday we had a little discussion about a job we're currently on.

80 year old brick commercial building. First floor has a small gift shop that was remodeled recently. The second story is being remodeled in two stages. Bare with me here. This will be a double occupancy short term rental sharing a kitchen. (Overflow for the B&B next door) What the owner wants is a complete rewire but plans to fir out all exterior walls for added insulation next year. However wants to rent it out this summer for income. We're able to get into all interior walls. I had thought about piping the ext walls and just tear it out on the second phase remodel but it seemed a big waste. My new partner suggested MC/1900's with enough slack to move the boxes out after the second phase framing but I disagreed thinking we could not have the MC exposed like that. Out came the code book.

MC Uses permitted Exposed or Concealed
MC Uses not permitted"will not be used in the following corrosive destructive environments. 1. Exposed to physical damage

It's that wording the confused me, "corrosive destructive". Do they mean "corrosive or destructive"? Or if it's in a corrosive environment, it can't be exposed to physical damage.
 
If you piped it in and set 1900s, you could just change the mudring out to a deeper one when the walls get firred and drywalled.

I agree if the AHJ would go with it I would just MC to 1900, use an industrial cover or something, then change the mudrings out before it gets drywalled. I don't see any reason to do this twice whichever way you go.

You could also sleeve the MC wall drop in EMT to avoid a total pipe job.
 