I remember reading some rules for mc wiring to flourescent fixtures in lay in ceilings, but i cant seem to find them in 330 or 410. I'm trying to find max length for a fixture whip. Can you guys help?
330.30(D) Unsupported Cables. Type MC cable shall be permitted to be unsupported where the cable:
(2) Is not more than 1.8 m (6 ft) in length from the last point of cable support to the point of connection to a luminaire (lighting fixture) or other piece of electrical equipment and the cable and point of connection are within an accessible ceiling. For the purpose of this section, Type MC cable fittings shall be permitted as a means of cable support.
Dave58er said:support isnt the problem. my boss is telling me I cant run mc for more than 6 feet between fixtures, support or otherwise. but i cant find that in the code.
infinity said:Dave58er said:support isnt the problem. my boss is telling me I cant run mc for more than 6 feet between fixtures, support or otherwise. but i cant find that in the code.
You can't find it because he's wrong. Tell him to read the Article that I've posted.
BUT...is the boss saying that because of local ordinace or job spec?
I dont't see where the OP said that the boss said it was a code issue
MC whips can be any length if they contain the same size conductors as the branch circuit. However, their last unsupported length can't exceed 6'.
Shockedby277v said:MC whips can be any length if they contain the same size conductors as the branch circuit. However, their last unsupported length can't exceed 6'.
Wow, those 1000' spools we're using would have some voltage drop! And that would be a lot of caddy clips.