Having read 200-6 on identification of conductors would anyone consider it a terrible offense to use 12/4wg mc cable(red,black,blue,white,green) for two circuits with separate neutrals by using the blue conductor as the second neutral? Would any of you inspectors turn it down?
Brian
 
Re: mc four conductor

Pierre: Reference 250.119. Where does it state the blue wire can not be re-identified, and used as a neutral?
 
Re: mc four conductor

200.6(E) would not permit this installation unless conditions of maintenance and supervision ensure that only qualified persons service the installation.

MC cable is available with separate grounded conductors for each ungrounded conductor. You can also get super neutral MC that has an over sized grounded conductor.

[ June 11, 2003, 11:58 PM: Message edited by: curt swartz ]
 
Re: mc four conductor

Thanks Bennie, I am glad someone is awake, 250.119 is EGC, and the question addresses a neutral conductor.

200.6(A)&(E) can be referenced as to the allowance of reidentifying the phase colored conductor for a grounded conductor.

Pierre
 
Re: mc four conductor

Curt and Pierre: You are correct. However there is no way an installation can be assured to only be serviced by qualified persons.
The rule is impossible to enforce, therefore it should be deleted from the book.

[ June 12, 2003, 12:13 AM: Message edited by: bennie ]
 
Re: mc four conductor

Bennie

I agree with you but if I didn't include the exception in my post someone would have brought it up. :)
 