Greg, may we congratulate on your success
(joking, of course)
Gus thank you very little......hahaha..
Greg, may we congratulate on your success
(joking, of course)
Why would you want to? The Al. bond strip #10 is in contact with the clad's entire length and simply cut it off after roto stripping the clad then install the listed connector.....no termination of bond strip required.
Instead of the term ground, which now means "the earth" I prefer the use of 'conductive path".
You as an inspector should be able to identify a code compliant instalation. Reason #2Why would you want to? The Al. bond strip #10 is in contact with the clad's entire length and simply cut it off after roto stripping the clad then install the listed connector.....no termination of bond strip required.
250.118.10 (2005) gives you the criteria for using MC cable sheath as a grounding conductor.I was told that I can use the jacket of an MC wire for a safty ground. ---
You as an inspector should be able to identify a code compliant instalation. Reason #2