MC to EMT fitting

Status
Not open for further replies.
A flex 90 is being used in lieu of a box.


Romex or mc was in the hand book commentary not the NEC code, commentary is opinion, and only applies when it agrees with me. :D


(F) Fitting. <---- So you interpret this as a flex 90 only? Im not trolling, I am just trying to figure out if what I had mentioned in an earlier post is a code violation.
 
Me from post 12:D
This was the gist of the Debate, is it listed to be used that way, Now I personally think it is safe and fine. I would rather use a fitting made for the purpose to avoid the argument with an inspector that may see it differently. I know Joe T has an issue with that type of use and he is not alone in his oppion so I am glad to see a fitting that makes it possible avoid these conflicts. Now Bridgeport can lobby the CMP to make it an out right violating to use the 3 fitting method.:D

This article in EC&M magazine says its a violation of 300.15 or 300.16 and the fittings are exposed.

http://ecmweb.com/nec/whats_wrong_here/electric_whats_wrong_63/

I think it's a stretch but the coupling are not listed for the use.

What do you think?

Article written by Joe T. :D
 
Your average "Joe" gets his facts wrong all the time, but I have a little more faith in publications like EC&M.

Look again at the author of your article you posted. That is the Joe T. I am referring to.
 
What about the same for NM? Hasn't it been discussed that the transition from EMT to cable that the fitting needs to be designed for the purpose? Listed even?

It's been discussed to death, Joe T will tell you it is a violation, I do not agree.
 
I've not used that fitting, but I've seen it in use lately. Surface mounted panel, pipe to just above the dropped ceiling, then MC from there to where ever. Makes for a slicker looking install. You just need to skin out the MC another 5 feet longer to go down to the panel. I don't know how much that fitting is, but I wouldn't be surprised if they weren't 5 bucks a piece.

What about the marking on the wires?
Is'nt this why NM can't be striped and the conductors used?
I know this has been discussed to death.
 