The NEC says that MC cable can be in a wet location if the conductors are listed for use in wet locations. So - MC Tuff cable has THHN/THWN conductors, but the website says the following:
"Outdoors or in wet locations where the armor has an overall outer, moisture resistant PVC jacket and the conductors are wet rated"
The website also says:
"THHN/THWN (XHHW available by order subject to lead time and minimum quantities)"
I don't understand. Can I used MC Tuff (Galvanized steel armor and THWN conductors) in a wet location (no outer PVC jacket)?
Edited to add:
I also found this on the AFC website:
"In wet locations where any of the following conditions are met:
— The metallic covering is impervious to moisture
— A lead sheath or moisture-impervious jacket is provided
under the metal covering
— The insulated conductors under the metallic covering are
listed for use in wet locations and a corrosion-resistant
jacket is provided over the metallic sheath"
which looks similar to wha's in my 2005 NEC, but is DEFINTELY not the same.
Thanks,
Mark
"Outdoors or in wet locations where the armor has an overall outer, moisture resistant PVC jacket and the conductors are wet rated"
The website also says:
"THHN/THWN (XHHW available by order subject to lead time and minimum quantities)"
I don't understand. Can I used MC Tuff (Galvanized steel armor and THWN conductors) in a wet location (no outer PVC jacket)?
Edited to add:
I also found this on the AFC website:
"In wet locations where any of the following conditions are met:
— The metallic covering is impervious to moisture
— A lead sheath or moisture-impervious jacket is provided
under the metal covering
— The insulated conductors under the metallic covering are
listed for use in wet locations and a corrosion-resistant
jacket is provided over the metallic sheath"
which looks similar to wha's in my 2005 NEC, but is DEFINTELY not the same.