I want to use MC cable for the feeder to a mobile home. Is the space underneath a mobile home considered "under a building" per Table 300.5? Do I have to install the MC in conduit or can I just direct bury it?
I feel that 300.5(C) would require that you have the MC cable installed in a raceway where it is under the mobile home.
Chris
Chris..........Wouldn't 330.10 (4) allow the MC under the mobile home to be exposed? I'm envisioning the DB MC emerging from the ground and running on the surface of the underside of the mobile home and then up into the loadcenter.
Isn't it (almost) always?The equipment grounding conductor of your MC Cable may have to be insulated.
Why cant MC Cable me use under a mobile home. I dont think op is stating it is under the ground
I want to use MC cable for the feeder to a mobile home. Is the space underneath a mobile home considered "under a building" per Table 300.5? Do I have to install the MC in conduit or can I just direct bury it?
Actually the OPer was asking about direct burying the MC cable.
Chris