Yes that can save you having to set up 13 reels. You can also make two pulls in the 1" EMT.
Then you need additional wire colors (may as well pull all at one time) or wire-marking/tagging.

This is what I mean. There are advantages and disadvantages to alternate ways of doing things.

That's why we have these discussions; to share and compare various methods and their merits.

Example: two home runs allows for J-boxes in different places, which may or may not be helpful.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
I like pipe over cable when its available. Trying to keep cable looking neat over longer spans can be more difficult adding time = labor costs, of course T&M it wouldn't matter (only to the customer).
2 pipes to avoid the Derating issues.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Then you need additional wire colors (may as well pull all at one time) or wire-marking/tagging.

This is what I mean. There are advantages and disadvantages to alternate ways of doing things.
Sure there are typically 10 ways to do the same task. Even if you split it into two raceways you would still need to mark the wires. I'm guessing that the cost of running two raceways is more than running one with #10's instead of #12's.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
To your initial question, my rule of thumb is 2 circuits, MC is practical, over 2 circuits and conduit and wire are the default. The factors that ALL need to be considered, are material cost, manhours, ease of installation, and yes the workmanship aspect.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Sure there are typically 10 ways to do the same task. Even if you split it into two raceways you would still need to mark the wires. I'm guessing that the cost of running two raceways is more than running one with #10's instead of #12's.
Way too many variables to say one outweighs the other. With 2 raceways, you get closer to your final destination with each run if properly planned. With rack and one piece strut straps, the labor for the straight portion of the runs is greatly reduced, just having and handling the additional spools and weight per spool of wire and having the availability of the the "carts" and the space to setup the 13 spools of #10 2000 foot rolls. In most case over the long haul of f project, I am going with 3/4" with maximum of 4 circuits per conduit.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
He's saying that with two raceways you can run #12 AWG instead of a single raceway with #10 AWG. Personally I'd opt for the single 1" and the #10's.
If you shared a neutral with (3) circuits each, you could use #12's and only have (9) conductors. Depending on the loads, the neutrals might be considered as non- current carrying.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you shared a neutral with (3) circuits each, you could use #12's and only have (9) conductors. Depending on the loads, the neutrals might be considered as non- current carrying.
True and back in the day that's the way we would always do it. I'm guessing that MWBC's are not allowed for this installation.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Way too many variables to say one outweighs the other. With 2 raceways, you get closer to your final destination with each run if properly planned. With rack and one piece strut straps, the labor for the straight portion of the runs is greatly reduced, just having and handling the additional spools and weight per spool of wire and having the availability of the the "carts" and the space to setup the 13 spools of #10 2000 foot rolls. In most case over the long haul of f project, I am going with 3/4" with maximum of 4 circuits per conduit.
Like I said there are 10 ways to do this. You've made some assumptions like that they'll be using heavy 2000' reels of wire instead of 500' reels. With a single raceway you certainly wouldn't have to pull in all 6 circuits at one time.

For us on commercial jobs #10 stranded homeruns in 1" or 1.25" EMT are pretty much standard.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Like I said there are 10 ways to do this. You've made some assumptions like that they'll be using heavy 2000' reels of wire instead of 500' reels. With a single raceway you certainly wouldn't have to pull in all 6 circuits at one time.

For us on commercial jobs #10 stranded homeruns in 1" or 1.25" EMT are pretty much standard.
I wasn't arguing with you, I was agreeing with you "way too many variables" My items weren't assumptions they were just some of the considerations and drawbacks and indicating that for us, all things considered, the fall back is 3-4 circuits. Another thing in my area, most engineers spec out maximum 3 homeruns in a conduit. Not always, just usually.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If you shared a neutral with (3) circuits each, you could use #12's and only have (9) conductors. Depending on the loads, the neutrals might be considered as non- current carrying.
That's always been my preference, until the handle-tie proponents effectively made it impracticable.
 

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
True and back in the day that's the way we would always do it. I'm guessing that MWBC's are not allowed for this installation.
I always wondered why it’s not actually mandatory for most jobs to save on vd and wire to meet the energy efficiency they always spout about
That's always been my preference, until the handle-tie proponents effectively made it impracticable.
Was it the handle ties that phased it out or those dumb afci breakers. Atleast those killed it in resi.
 