MCA 20.5 AC equipment

Status
Not open for further replies.

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
I often see minimum circuit ampacity for AC equipment listed: 20.5 amp or 30.5 amp.
Is that just the way the math works or are they wanting a larger conductor?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Most likely how the math works. There are rules in the product standard that specify how the calculation is to be made.
 