Looked at this today. AC unit with MCA=43.9 amps, MaxOCPD=60 amps. Engineer specified #6 THHN in EMT with a #10 EGC. Since #8 THHN is a 50 amp conductor my first assumption was that the EGC has to be up-sized to a #8 when installed with the #6 ungrounded conductors. Thoughts?