- New Jersey
- Journeyman Electrician
I did not read that you must use the 60C rating, I inferred it based on this
60C is the minimum size required-- a #4 wire does not care if it has 60C or 90C temp rating for a fault. The capacity of the #4 is really limited because of the temp of the insulation. In theory we should always use the 90C rating but the statement above says the minimum size. I think the changes creates more trouble then it will fix.
I assume the reason we can use smaller conductors for the egc is because the conductors themselves can carry the faults and the insulation should not come into play. Just a thought.
Wouldn't 75? C terminations at both ends and a 75? C conductor be the minimum size? Using 60? C would give you a larger size conductor.