Do you think 220.5(b) applies to MCA values?30 amps is less than 30.25 so IMO the #10 is too small.
No. That only applies within Article 220 for load calculations. There was a Public Input to move that rule to Article 110 so it would apply throughout the code and that was rejected. The language in the 2026 code specifically says load calculations.Do you think 220.5(b) applies to MCA values?
The calculation in this thread is an ampacity calculation and not a load calculation.120.5 (B) Fractions of an Ampere.
Load calculations shall be permitted to be rounded to the nearest whole ampere, with decimal fractions smaller than 0.5 dropped.
No. That only applies within Article 220 for load calculations. There was a Public Input to move that rule to Article 110 so it would apply throughout the code and that was rejected. The language in the 2026 code specifically says load calculations.
The calculation in this thread is an ampacity calculation and not a load calculation.
Note that Article 220 in previous codes became Article 120 in the 2026 code.
If it's important, I would be inclined to check the listing standards to see if the load is actually being calculated to more than two significant figures. If not, rounding down would be justifiable on a technical basis, and then I'd check for any (irrational) code prohibitions.Rounding down the 30.25 would not be allowed because it's considered double dipping
A MCA calculation is never a load calculation, It is the calculation that gives you the minimum ampacity of the circuit conductors for that circuit.What I think you're saying is that the MCA value is derived from the load calculation.