MCB to turn AC motors on and off.

Thanks, I've never dealt with this before.
So where do you pick up the B phase? Does it land in the panel, without landing on the breaker, or in a bucket without landing on OCPD?
Hard for me to picture how the phase conductor is ran to the disconnect, or control.
It's is simply a grounded conductor. It is treated just like the typical neutral you are used to, in fact it should even be white of gray.
 
Thanks, I've never dealt with this before.
So where do you pick up the B phase? Does it land in the panel, without landing on the breaker, or in a bucket without landing on OCPD?
Hard for me to picture how the phase conductor is ran to the disconnect, or control.
It's three phase delta with a "neutral" but without a fourth wire. When you put your meter B to ground you get 0V instead of 480V.
 
If that 30 amp is providing ground-fault short circuit protection for the motors as it appears to be, it is oversized for the 3HP motor.
 
Besides, there is an overload relay attached to the motor contactor.
This is what motor starters are made for, they are typically designed for at least 1,000,000 electrical operations, as opposed to the 6,000 of a circuit breaker. Makes no sense that they use the breaker AS a motor starter, when they HAVE a motor starter!

Someone is being lazy. What’s the point of asking how long they can get away with this laziness? Just let them suffer the consequences, maybe it will foster a change in their behavior…
 
Thanks, I've never dealt with this before.
So where do you pick up the B phase? Does it land in the panel, without landing on the breaker, or in a bucket without landing on OCPD?
Hard for me to picture how the phase conductor is ran to the disconnect, or control.
It is the grounded conductor, it must be bonded at the service equipment or either the source or first disconnect if separately derived system. You treat it exactly like you do a grounded neutral on most any other system.

Sorry I see there were more posts that covered this. I happened to be right at page break before replying.
 
This is what motor starters are made for, they are typically designed for at least 1,000,000 electrical operations, as opposed to the 6,000 of a circuit breaker. Makes no sense that they use the breaker AS a motor starter, when they HAVE a motor starter!

Someone is being lazy. What’s the point of asking how long they can get away with this laziness? Just let them suffer the consequences, maybe it will foster a change in their behavior…
Isn't NEMA contactors typically million operations and IEC typically 500k in their specifications?
 
Since OP has motor starters, the breaker in question is breaking the load when he turns it off. Unless the control voltage comes from elsewhere the breaker isn't exactly closing into a motor trying to start as it would first be energizing the contactor coil and the contactor would be taking the beating of closing under motor starting current.
 
Isn't NEMA contactors typically million operations and IEC typically 500k in their specifications?
No, especially if they are both tested to UL standards.

The difference between IEC and NEMA is the amount of load each is rated for. For example a NEMA Size 1 starter is actually rated for 27A, quite a bit more than a standard10HP 480V motor so it lasts forever, compared to a 10HP IEC that is rated for only 15A. If you used a 30A IEC it would last as long as the NEMA.

The cheap stuff is the Definite Pupose contactors.
 
I try find reason for excessive size mcb regard to 3 hp motor Assuming op aware code maximum size, reason for beyond that size may be use Q0 square d mcb it not meeting code maximum size nuisance tripping otherwise.
 
Overload relay for motor op#4, overload relay ocpd
Overload relays are not standalone branch circuit OCPD.

The OP refers to individual disconnects but does not say if they contain OCPD. Based on the supplied information it appears the QO breaker is the OCPD for both motors.
 