MCB Tripping Issues During PC Startup – Inrush Current Problem?

sareehy

New User
Location
Irbid
Occupation
Electrical technician
Hello All,

I’m facing an issue with MCBs tripping during computer startup and would appreciate your technical insights. Here are the details:

Case 1:
We have a sub-circuit MCB C32 supplying power to 8 desktop PCs. Occasionally, the breaker trips immediately after startup.

Case 2:
At another location, 30 PCs are connected across two sub-circuit MCBs (C32 each), with the main distribution panel protected by an MCB C100. Here, the main breaker trips immediately after startup, sometimes with a visible spark. The sub-circuit breakers also trip occasionally.

Observations:
Current measurements show a significant spike during startup before tripping occurs.
When PCs are completely disconnected from power (by unplugging their power cords ), no tripping issues occur.

Questions:
1. Is this behavior likely caused by excessive inrush current during PC startup?
2. What are the recommended solutions to prevent these nuisance trips?

Best regards,
 
PC power supplies will have a significant inrush current when first powered up as the capacitors in the SMPS charge up. When I was doing power supplies, I once saw a 400W PSU draw 29A on initial turn-on. In good PSU designs, they take steps to limit this inrush current, often using NTC resistors or current limiting resistors and a bypass relay. If these were working fine for a while and started exhibiting this behavior, it might be that the inrush protection circuits have broken down over time or were damaged by a surge or something. That might spell trouble for the PSUs as well, because the capacitors will damage themselves. If this is a first time situation, you may need to change the way you power them, i.e. fewer PSUs on each breaker, or maybe breakers with a trip curve more tolerant of high inrush, like a D curve.
 