An engineering firm was contracted to perform the analysis. The labels were made specifically for the equipment.
To rephrase the question, shouldn't each bucket have its own label? For example, a section in one MCC has a flash hazard of 306 cal/cm^2 (the section with the main is 37017). So as of right now, I would have to disconnect the entire MCC just to replace a fuse in a bucket that is still in place?
I took this to mean the section with the main was determined to have an AFC of 37,017A (37kA), which came out to 306 cal/cm2. Makes more sense that way... (actually, looking at it again I guess I should say it makes less nonsense...)
But to your point, does it mean that you must kill the entire MCC bus to change a fuse in a bucket?
No, but you will have to suit up to the appropriate PPE and get a Hot Work Permit.
This is why MCC mfrs are coming out with the ability to disconnect a bucket from the bus, not just open the breaker. What those options do is to significantly limit the exposure to live parts and minimize the time to remove and replace buckets, because the entire bucket, including the stabs, are no longer in contact with anything live and it can be verified from the outside prior to opening the door. Many places are precluding the need for the HWP if it can be documented that there are no live parts inside.
But even then, you cannot open the door if the bus is live without suiting up to the appropriate PPE for the HRC, because you will still be in the Restricted Approach Boundary area (typically 1 ft. for 480-600VAC) of that live bus, even if it is behind an insulator and shutters. Those are electrically safe, but will not even slow down an arc blast if one happens behind them or even in another section sharing the air space. So that usually means PPE 4, even if only for a minute.