To be 150HP or 200HP
To be 150HP or 200HP
I have a switchboard feeding 480V MCC sections with 800A main lugs via a parallel feed. This section includes 3 - 150HP pump motors, then a 40HP and some random 5HP buckets.
I verified with the control systems team and there is a delay of 5 seconds between the 3 200HP motors.
FLA of 200HP is 240A +/- specifics
FLA of 150HP is 180A +/- specifics
The motors at 150hp might be ok on the 800A main fusing .... But if I understand if they are 200hp I think the calculations are shy for 800A main fusing..
Or 200hp was reported in error in your latest post...