I have a reversing motor contactor for a large (300HP, 480VAC). It came with an MCP in the cabinet. It is fed directly from an adjustable branch circuit breaker. This motor has to be estopped within 2 seconds. Plugging is used for this.
When the motor is E-stopped 10 minutes after starting, all is well.
When it is E-stopped (plugged) within 5 minutes of starting, the MCP trips. It's max setting is 5000A. The FLA is 345A. I believe the max amps which should be seen for plugging should be something a little in excess of locked rotor. The windings are type G. 1800A+ maybe as high as 2300V. It should not be tripping. In fact, when we jumpered out the MCP, the upstream breaker held even when the motor was started and estopped multiple times within a half hour period.
We suspect that the MCP is not able to clear heat fast enough after a start to handle the plugging inrush. OR, it is a bad MCP.
My question is this. Is the MCP actually required. It is at the contactor on a mezanine above the production line where the motor is. The upstream breaker is about 200 ft away in a mechanical/electrical room.
Can we not just replace the MCP with a non-fused disconnect?
When the motor is E-stopped 10 minutes after starting, all is well.
When it is E-stopped (plugged) within 5 minutes of starting, the MCP trips. It's max setting is 5000A. The FLA is 345A. I believe the max amps which should be seen for plugging should be something a little in excess of locked rotor. The windings are type G. 1800A+ maybe as high as 2300V. It should not be tripping. In fact, when we jumpered out the MCP, the upstream breaker held even when the motor was started and estopped multiple times within a half hour period.
We suspect that the MCP is not able to clear heat fast enough after a start to handle the plugging inrush. OR, it is a bad MCP.
My question is this. Is the MCP actually required. It is at the contactor on a mezanine above the production line where the motor is. The upstream breaker is about 200 ft away in a mechanical/electrical room.
Can we not just replace the MCP with a non-fused disconnect?