190801-2131 EDT
This thread is related to making troubleshooting measurements.
This post is about some ground (earth surface) measurements. These are surface measurements between two screwdrivers measured with a Beckman 4.5 digit AC DVM. There is no filtering except the bandwidth of the meter which is about 30 kHz. This is a high input impedance meter, and that is what is wanted. This basically removes errors from probe to earth resistance. An input series capacitor eliminates any DC component. The distance between probes is about 12 feet.
1. At a location directly above my copper water line, and parallel to it, that is nearly 8 feet deep was about 2 mV.
2. Same as 1 except one probe was moved to make the path perpendicular to the water line, about 6 mV.
3. Picked another location below my 3 phase power lines that is 30 ft from the water line. My 3 phase primary has no neutral. Read about 8 mV.
4. Put one probe close to power pole where my transformer is located to sense close to the transformer ground rod. The second probe was 12 feet away in a direction toward my meter on the side of the house. The meter location is very close to where the copper water line enters and which is used as the house ground rod. Read about 250 mV.
Whenever one makes a voltage or current measurement there is a one turn coil involved in that measurement loop. In an AC measurement there can be induced a signal that may interfere with the desired measurement. The size and shape of that one turn loop may not be well defined. The magnitude and frequency of any magnetic field coupling to the one turn coil is of concern.
Just taking my two leads and forming a circle where I am sitting the unwanted signal is less than 10 microvolts, the meter noise level is this 10 microvolt level.
At my home I generally assume this unwanted error signal is zero and I don't test for it.
Ground voltage measurements generally jump around some depending what local loads are changing. To this are changes from remote current sources, possibly many miles away.
At one time I looked for some 50 Hz. Did not see any, but better instrumentation might make it possible to see some. But I did think I saw a component at a much lower frequency. Don't remember the details.
.
This thread is related to making troubleshooting measurements.
This post is about some ground (earth surface) measurements. These are surface measurements between two screwdrivers measured with a Beckman 4.5 digit AC DVM. There is no filtering except the bandwidth of the meter which is about 30 kHz. This is a high input impedance meter, and that is what is wanted. This basically removes errors from probe to earth resistance. An input series capacitor eliminates any DC component. The distance between probes is about 12 feet.
1. At a location directly above my copper water line, and parallel to it, that is nearly 8 feet deep was about 2 mV.
2. Same as 1 except one probe was moved to make the path perpendicular to the water line, about 6 mV.
3. Picked another location below my 3 phase power lines that is 30 ft from the water line. My 3 phase primary has no neutral. Read about 8 mV.
4. Put one probe close to power pole where my transformer is located to sense close to the transformer ground rod. The second probe was 12 feet away in a direction toward my meter on the side of the house. The meter location is very close to where the copper water line enters and which is used as the house ground rod. Read about 250 mV.
Whenever one makes a voltage or current measurement there is a one turn coil involved in that measurement loop. In an AC measurement there can be induced a signal that may interfere with the desired measurement. The size and shape of that one turn loop may not be well defined. The magnitude and frequency of any magnetic field coupling to the one turn coil is of concern.
Just taking my two leads and forming a circle where I am sitting the unwanted signal is less than 10 microvolts, the meter noise level is this 10 microvolt level.
At my home I generally assume this unwanted error signal is zero and I don't test for it.
Ground voltage measurements generally jump around some depending what local loads are changing. To this are changes from remote current sources, possibly many miles away.
At one time I looked for some 50 Hz. Did not see any, but better instrumentation might make it possible to see some. But I did think I saw a component at a much lower frequency. Don't remember the details.
.