I'm trying to get a project finished up involving a new fuel system with a cardlock controller. The cardlock controller instructions state specifically that my neutral-ground resistance measured at the cardlock with power on, must be less than 1 ohm or it will cause issues with the memory and transaction data they need to store.
Here's where I'm starting to question my methods. I have a brand new Fluke 289 that has been used possibly 5 times. My resistance reading is .258-.4xx ohms using the 50 ohm, low ohm setting. I'm good, right?
The fuel system tech puts his fairly new Fluke 117 in there and gets 5.5-8ish ohms, depending on which time we were testing. He also had another Ideal meter that I didn't catch the model of, that had similar readings within a couple ohms.
I'm trying to understand if that error comes from the different accuracy levels of each meter or something else I'm not thinking of? The fuel tech is adamant there is a resistance issue, of course I think just the opposite. I should mention that swapping leads, made almost zero difference. Terminals are nice, clean and tight. The test probes/clips were put in the same spot everytime, just to rule out some variables.
http://en-us.fluke.com/products/digital-multimeters/fluke-117-digital-multimeter.html#techspecs
http://en-us.fluke.com/products/digital-multimeters/fluke-289-digital-multimeter.html#techspecs
I'd appreciate it if someone could take a peek at both meters specs and let me know if the accuracy for each meter is enough to cause that big of a discrepancy? I can't tell by the specs if accuracy is a percentage of the meters range or a percentage of the tested result? At this point, I'm about to send my 289 in to have a fresh calibration done, just to cover my bases and assure the customer this installation is correct. I may just call Fluke tomorrow and ask them about the accuracy as well as possible calibration, but I figured some of you guys on here could get me pointed in the right direction.
Thanks.
Here's where I'm starting to question my methods. I have a brand new Fluke 289 that has been used possibly 5 times. My resistance reading is .258-.4xx ohms using the 50 ohm, low ohm setting. I'm good, right?
The fuel system tech puts his fairly new Fluke 117 in there and gets 5.5-8ish ohms, depending on which time we were testing. He also had another Ideal meter that I didn't catch the model of, that had similar readings within a couple ohms.
I'm trying to understand if that error comes from the different accuracy levels of each meter or something else I'm not thinking of? The fuel tech is adamant there is a resistance issue, of course I think just the opposite. I should mention that swapping leads, made almost zero difference. Terminals are nice, clean and tight. The test probes/clips were put in the same spot everytime, just to rule out some variables.
http://en-us.fluke.com/products/digital-multimeters/fluke-117-digital-multimeter.html#techspecs
http://en-us.fluke.com/products/digital-multimeters/fluke-289-digital-multimeter.html#techspecs
I'd appreciate it if someone could take a peek at both meters specs and let me know if the accuracy for each meter is enough to cause that big of a discrepancy? I can't tell by the specs if accuracy is a percentage of the meters range or a percentage of the tested result? At this point, I'm about to send my 289 in to have a fresh calibration done, just to cover my bases and assure the customer this installation is correct. I may just call Fluke tomorrow and ask them about the accuracy as well as possible calibration, but I figured some of you guys on here could get me pointed in the right direction.