Medium Voltage Calbe in Cable Tray

Merry Christmas
Status
Not open for further replies.

brandtew

Member
our electrical contractor has been told that he cannot use 15KV cable single conductors in a cable tray. He was told that this is not permissible by the NEC. That the cable must be Armored Cable. However I have not found anything in the NEC 2008 that prevents him from using 15KV cable EPR insulation 133%, tapped shield, 90 C, TC, sunlight resistant, PVC outer jacket in a cable tray. Could someone let me know who is right I appreciate it
 
Medium voltage cables (Type MV) up to 35kV are specifically permitted to be used in cable trays. See Sections 328.10(3), 392.3(B)(1), 392.12 and 392.13(B).
Note: Identified does NOT necessarily mean listed or labled for the specific application.
 