our electrical contractor has been told that he cannot use 15KV cable single conductors in a cable tray. He was told that this is not permissible by the NEC. That the cable must be Armored Cable. However I have not found anything in the NEC 2008 that prevents him from using 15KV cable EPR insulation 133%, tapped shield, 90 C, TC, sunlight resistant, PVC outer jacket in a cable tray. Could someone let me know who is right I appreciate it
 
Medium voltage cables (Type MV) up to 35kV are specifically permitted to be used in cable trays. See Sections 328.10(3), 392.3(B)(1), 392.12 and 392.13(B).
Note: Identified does NOT necessarily mean listed or labled for the specific application.
 