Medium Voltage Capacitors
bnewport
Indiana
In a medium voltage substation with a grounded capacitor bank, how much current would normally flow to ground? Other than testing the de-energized caps with a Fluke meter, how can I determine what is causing the current and if it is acceptable?
Bryan
Re: Medium Voltage Capacitors
Capacitor load is no different that any other 3 phase load when speaking of load flow. If the caps are ok the 3 phase load should cancel and there should be no neutral current. What problems are you having? ARe you taking a clip-on reading at the neutral connection to the caps?
Don't forget harmonic currents. They flow to capacitor banks.
[ May 13, 2005, 12:37 PM: Message edited by: bob ]
Bob-
I am not having any problems...yet... I have to go next week to check substation grounding. The details are minimal so far, but I guess they have about 7 amps on the ground, even with the caps offline. I need to track down this source of ground current. I am not a high voltage guru, so I am not sure where to begin. Any ideas?
Bryan
Let me start with:
I have absolutely no experience with the kind of applications you're talking about. But.
This is how to calculate capacitive reactance:
1/2PifC or
1/((2)(Pi)(frequency)(caqpacitance))
The reciprical of 2 x 3.141 x 60 Hz. x (capacitance in Farads)
This is the impedance of a capacitor.
An Example.
A 6.7 MF capacitor shunted across a 60 Hz. sourse.
1/6.283 x 60 x .000,0067
1/.002526
396 ohms impedance.
At 600 volts:
600/396 = 1.515 amps.