Medium Voltage electrical conductor

Status
Not open for further replies.

mathan1987

Member
Location
Seattle
Occupation
Electrical design engineer
Hi,

For the medium voltage cables in the underground duct banks how do we calculate the derating of the conductor capacity for the soil resistivity?
what are the softwares I can use to calculate the soil resistivity adjustments.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
Sorry. According to IEC 60364-1:
circuits supplied at nominal voltages up to and including 1 000 V a.c. or 1 500 V d.c.;
For medium voltage it is IEC 60502-2.
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
For software, check out AmpCalc. It does a Neher-McGrath calculation for duct bank derating that should be consistent with the NEC. It's been around a long time. If this is a one-off, you can also just ask cable suppliers to do the calculation for you - Okonite or Southwire have been willing to do this - at least in the past.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
See IEC 60502-2 Table B17
 

Attachments

  • IEC 60502-2 Table B17.jpg
    IEC 60502-2 Table B17.jpg
    105.7 KB · Views: 7