Medium Voltage Feeder Through a Building

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
... In OP case if he runs the cable actually outside the first building, no need for disconnecting means on the first building. What do you think?
If the conductors are entirely outside the first building, then a disconnecting means for the first building is not required.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
That is done beginning at the construction stage of the building itself and not after the building construction is over. In OP case if he runs the cable actually outside the first building, no need for disconnecting means on the first building. What do you think?

I would agree then, no disconnecting means.
 

iwire

Moderator
Staff member
Location
Massachusetts
I would be very surprised if an AHJ would allow a MV feeder to pass through a building without following part II of 225 even if encased inside the slab from the start.
 

Sahib

Senior Member
Location
India

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Not necessarily. A feeder circuit starts from the load side of a disconnecting means. The cable staring from secondary side of transformer of OP till it is terminated in a disconnecting means is not so much a feeder cable as a service cable.The provision of Art.225 part II applies to feeder/branch circuits:

http://www.jade1.com/jadecc/courses/UNIVERSAL/NEC05.php?imDif=2554.0

If its from the utility I would agree, if not I would say a branch feeder.


BTW, the disconnect in that link is wired wrong :(
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
That is done beginning at the construction stage of the building itself and not after the building construction is over. ...
I have seen pictures of it being done after the building has been completed....they built form work around the conduit and poured concrete to a thickness of at last 2" all the way around the conduit. Of course a few extra supports were added to carry the additional weight of the concrete.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Not necessarily. A feeder circuit starts from the load side of a disconnecting means. The cable staring from secondary side of transformer of OP till it is terminated in a disconnecting means is not so much a feeder cable as a service cable.The provision of Art.225 part II applies to feeder/branch circuits:

http://www.jade1.com/jadecc/courses/UNIVERSAL/NEC05.php?imDif=2554.0
You can have feeder cables on the secondary side of the transformer as long as that transformer is on the load side of the service disconnect.

Making the cable a service cable and not a feeder cable increases the installation restrictions.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I have seen pictures of it being done after the building has been completed....they built form work around the conduit and poured concrete to a thickness of at last 2" all the way around the conduit. Of course a few extra supports were added to carry the additional weight of the concrete.

Is the concrete mandatory?
 

iwire

Moderator
Staff member
Location
Massachusetts
I have seen pictures of it being done after the building has been completed....they built form work around the conduit and poured concrete to a thickness of at last 2" all the way around the conduit. Of course a few extra supports were added to carry the additional weight of the concrete.

Did it literally pass through the interior of a building without a disconnecting means?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Did it literally pass through the interior of a building without a disconnecting means?
It was actually service conductors to the service disconnect that was inside the building and not "nearest the point of entrance", but the same type of thing could be done with a feeder conductor passing though a building.
 

iwire

Moderator
Staff member
Location
Massachusetts
It was actually service conductors to the service disconnect that was inside the building and not "nearest the point of entrance", but the same type of thing could be done with a feeder conductor passing though a building.

Yes and I have done service conductors like that.

But unless I am mistaken the OP has a feeder leaving building 1, passing through building 2 and onto power building 3.

In my opinion a disconnecting means is required at building 2 regardless of concrete encasement.
 