I have a situation where my client has a main-tie-main distribution setup at 4160 volts. The tie is normally open. When doing maintenance on one main breaker or the other, they typically close the tie and then open whichever main that is scheduled for maintenance, thus for a few seconds, the power sources are paralleled.
I did some fault calculations. Each source has a fault contribution of 138 mVA. The breakers are older magna-blast units rated at 250 mVA. The combined fault exceeds the rating of the breakers, but if you draw the circuit on a piece of paper, the fault current through either main or either bussing will never exceed 138 mVA, except for the exact point where the fault exists. If the fault occurred due to a failure within the mechanism of the tie breaker, then I could see where this breaker may have a violent failure during an operation.
This client is considering replacing this and other similar substations over the next few years. Upgrading all breakers, including his feeders, to 350 mVA represents an upcharge that easily is in excess of $100,000. Is this necessary? My feeling at this time is to recommend that only the ties have a 350 mVA rating, and the busswork is braced for 350 mVA.
Thanks for your help!
I did some fault calculations. Each source has a fault contribution of 138 mVA. The breakers are older magna-blast units rated at 250 mVA. The combined fault exceeds the rating of the breakers, but if you draw the circuit on a piece of paper, the fault current through either main or either bussing will never exceed 138 mVA, except for the exact point where the fault exists. If the fault occurred due to a failure within the mechanism of the tie breaker, then I could see where this breaker may have a violent failure during an operation.
This client is considering replacing this and other similar substations over the next few years. Upgrading all breakers, including his feeders, to 350 mVA represents an upcharge that easily is in excess of $100,000. Is this necessary? My feeling at this time is to recommend that only the ties have a 350 mVA rating, and the busswork is braced for 350 mVA.
Thanks for your help!