The seperation between live parts is 6". The switchgear is 15kV.
The bus work is factory buswork, but the terminations are made in the field.
Should the connections be insulated?
Is it a violation of Table 490.24 if it is not (based on paragraph 490.24)?
490.24 Minimum Space Separation. In field-fabricated in-
stallations, the minimum air separation between bare live con-
ductors and between such conductors and adjacent grounded
surfaces shall not be less than the values given in Table
490.24. These values shall not apply to interior portions or
exterior terminals of equipment designed, manufactured, and
tested in accordance with accepted national standards.