Can you install 6 circuits (9 wires) of #12 thhn in one conduit under the following conditions:
I understand 240.2(B)(1) basically says a 20 amp circuit for receptacles must have a derated ampacity of
at least 20 amps?.So can I choose to use the 80% adjustment factors and meet code or the 70% and not
meet code
Given:
? 20 amp single pole breakers. The Engineers does not want to use 15 amp breakers (not concerned with handle tie code issue for now)
? 6 circuits in one conduit ? phase A,B,C, and N, Phase A,B,C and N, 1 equipment ground)
? Assume voltage at panel is 120/208 3 phase 4 wire
? Assume ambient temperature is 110 degrees F
? Assume there are four 120v duplex receptacles on each circuit.
? Application is high school classroom (not a computer lab)
Which do you do?:
? Do you derate for 4-6 conductors @ 80% (which will make the installation meet code) or
? for 7-9 conductors @ 70% because non-linear loads could theoretically be present at some point in the future. (which will not make the installation meet code
Step 1--------#12 thhn. 90 degree column = 30 amps x .87 for ambient temperature = 26.1 amp
Step 2--------26.1 amp x 80% (4-6 conductors ? neutral only carrying imbalance) = 20.88 amps MEETS
CODE
or
26.1 amp x 70% (7-9 conductors ? neutral carrying more than unbalance because nonlinear/harmonics
present) = 18.27 amps. DOES NOT MEET CODE
I understand 240.2(B)(1) basically says a 20 amp circuit for receptacles must have a derated ampacity of
at least 20 amps?.So can I choose to use the 80% adjustment factors and meet code or the 70% and not
meet code
Given:
? 20 amp single pole breakers. The Engineers does not want to use 15 amp breakers (not concerned with handle tie code issue for now)
? 6 circuits in one conduit ? phase A,B,C, and N, Phase A,B,C and N, 1 equipment ground)
? Assume voltage at panel is 120/208 3 phase 4 wire
? Assume ambient temperature is 110 degrees F
? Assume there are four 120v duplex receptacles on each circuit.
? Application is high school classroom (not a computer lab)
Which do you do?:
? Do you derate for 4-6 conductors @ 80% (which will make the installation meet code) or
? for 7-9 conductors @ 70% because non-linear loads could theoretically be present at some point in the future. (which will not make the installation meet code
Step 1--------#12 thhn. 90 degree column = 30 amps x .87 for ambient temperature = 26.1 amp
Step 2--------26.1 amp x 80% (4-6 conductors ? neutral only carrying imbalance) = 20.88 amps MEETS
CODE
or
26.1 amp x 70% (7-9 conductors ? neutral carrying more than unbalance because nonlinear/harmonics
present) = 18.27 amps. DOES NOT MEET CODE