billybandit
Member
- Location
- Greensboro NC
- Occupation
- electrical contractor
Due to missing dead fronts, I am replacing (fire marshal mandated) Zinsco combo meter panels installed during the original buildout of this apartment campus in 1975.
The existing Zinsco main breaker is 200 amps and the breaker feeding into individual sub panel units is 150 amps. I cannot find any information indicating Zinsco kaic greater than 10k.
The local utility has calculated MAFC for some of the laterals at 28k and 32k respectively (all others at 11k)
I am looking for a meter combo (minimum 6-8 spaces) or other service configuration to handle the 28k and 32k fault currents.
Pictures of the existing Zinsco configuration and 22k replacement configuration are attached.