Meeting Rooms. Opinions needed,
In Jan issue of ELECTRICAL CONTRACTOR Magazine, CODE FAQS, a reader asks the question "If Two duplex receptacles are installed in a 4-inch box in a wall, can I count that as Two receptacles outlets to comply with 210.65 for meeting rooms?..."
Author responds "NO" reciting definition of "Outlet"
I believe the intent of this section is to the number of wall receptacles required, and not the number of outlets required.
By the author's statement, a 1 gang box and a 6 gang box loaded with duplex receptacles would both count as a single receptacle outlet.
Appreciate your thoughts.
Thank you
Michael H.