Yes it works. Fluke used to sell an external resistor that you plugged in that was a 10k resistor. If the triac "off" state is say 100k and you apply 110 V and the meter resistance is 10k, the voltage that you read will be 110 x 10 / 110 or 10 V. If it is a 5k it will be 110 x 5 / 105 or very close to 5 V. Typical triac off resistance though is usually much higher. Either way if you are seeing 5 or 10 V you will still correctly conclude that the triac is in the off state (No voltage on the gate) where if it reads close to 100 V it is in the "on" state. In the same scenario with a 1 megaohm "HiZ" input in the metsr which is close to a typical FEF inout circuit you would see 110 x 1000 / 1100 or pretty close to 100 V and incorrectly assume the triac is "on" if there is no load on the triac when it's just the output voltage when the meter itself completes the circuit.


Sent from my SM-T350 using Tapatalk
 
Thanks & Fluke still make them. Between $65 $90 depending on supplier.
That's the one. If the Megger terminals have the same spacing and many meters do, you could plug it in the Megger.