I started to ask some questions in a previous post regarding megger operation but I figured I'd start a new thread to ask more specific questions.
Specifically I wanted to understand exactly how a megger functioned and how to reperestent the different parts of a megger with circuit equivelents.
So looking at my 1000V AMEC 1040 megger I notice that for 1000V DC it has a nominal output current of 1mA and a measurement range of up to 2000Mohms.
From the previous post it was stated that the current output in a megger is current limited and in my case it appears that its limited to 1mA. What is it that limits this output current to 1mA at 1000V? Output impedance?
I believe a Megger works by outputting this 1mA output current and measuring the voltage drop between leads in order to calculate a resistance? So does the unit always output 1mA regardless of what the measured circuit resistance is? What if measured circuit is a dead short?
It was also mentioned in previous post that voltage on measured circuit may be less than 1000V due to voltage drop across megger output. So when measuring at circuit does the primary point of the circuit actually see 1000V or is it less depending on output impedance and current?
I have seen some cases where when measuring a circuit the voltage will not increase, on an adjustable megger and will stay at a miniumum voltage. What is happening here? Is there not enough voltage in these cases to push the current?
I also assume that DC is used for this instrument to avoid issues with capacitance coupling in circuits.